Difference between revisions of "GeoLink Configuration"
(22 intermediate revisions by the same user not shown)
== <translate><!--T:1-->
Line 5: Line 6:
<translate><!--T:2-->
GeoLink is supported from firmware version 2.5. In order to utilize all the functions it is necessary to enable the support in the Spirit Settings - ''General tab'' first.
After enabling, save the settings and re-power the model.</translate>
Line 21: Line 22:
How to check</translate> ===
<translate><!--T:6-->
<translate><!--T:99-->
To verify that GeoLink is calibrated correctly for your area, please launch the ''Spirit Settings'' and open ''GeoLink settings'' window.
<!--T:6-->
Line 52: Line 56:
<!--T:14-->
<!--T:14-->
#The Status LED will be indicating progress of the calibration then. Start moving with the model in all possible directions and angles to mimic a sphere. Any LED flash will indicate that a new calibration data were acquired.
#Rotate with the module as long until you will see periodic LED flashing. At this point the calibration is finished. After following re-power the module is ready for operation.</translate><br/>
<!--T:111-->
</translate>
{{Info|[[File:Info.png|18px|]] <translate><!--T:15-->
For 600+ class helicopters we recommend to perform calibration while GeoLink is not mounted. In that way it can be more comfortable and easier.</translate><br/>[[File:Info.png|18px|]] <translate><!--T:16-->
Line 61: Line 71:
'''Spirit Setings will not see GeoLink''' during Calibration mode. Calibration will not finish until it is fully done. If power is turned off while calibration is not finished, the calibration process will start from the beginning after next power up.</translate>}}
=== Calibration Video ===
== <translate><!--T:18-->
Line 66: Line 81:
<translate><!--T:19-->
As the first step pilot has to decide what GeoLink feature he want to use. To find how each feature is working please visit [[GeoLink_Features|Features page]].
Pilot can enable multiple features at the same time if needed.
<!--T:20-->
<!--T:20-->
Check feature you would like to use in the Aid tab of the GeoLink window.
For the first tries we recommend to use a default values.</translate>
Line 78: Line 93:
<translate><!--T:22-->
You can verify if triggering mechanism is working correctly even before actual flight by checking the Aid tab.
If a feature is engaged you will see '''ACTIVE''' or in other case '''Inactive'''.</translate>
{{Quote|<translate><!--T:23-->
For safety reasons do not engage any GeoLink feature before model is in the air at appropriate altitude.</translate>}}
For safety reasons turn off all GeoLink features before lift off. Then in a safe altitude you can enable the feature carefully. All features can be instantly disengaged at any moment so you can continue in a normal flight.</translate>}}
Line 91: Line 106:
By default all GeoLink features are engaged as soon as a Stabi function is active. For example if Coaxial or Rescue mode is engaged the GeoLink feature is engaged as well and complement operation of a Stabi function by acting simultaneously.
We recommend to set Stabi/Function to '''Coaxial''' mode for Geo-fence, Return to Home and Position Hold features.</translate>
<translate><!--T:100-->
We recommend to use this way only when you are out of a free channels.</translate>
==== <translate><!--T:26-->
Dedicated GeoLink channel</translate> ====
Dedicated GeoLink channel [Recommended]</translate> ====
<translate><!--T:27-->
Alternatively you can assign a GeoLink feature to any free channel in the General/Channels window. In the right part of the Spirit Settings software select which feature you would like to assign. (for example '''F: Return to Home'''). Then select appropriate channel which will be used for engaging.
You can use same channel for multiple features at the same time.</translate>
== <translate><!--T:28-->
== GeoLink functions ==
Geo-fence</translate> ==
<translate><!--T:29-->
To enable this feature it is required to tick the CheckBox in the GeoLink window/Aid tab.</translate>
=== <translate><!--T:30-->
Usage</translate> ===
<translate><!--T:31-->
<!--T:32-->
# To engage with assigned GeoLink channel - it is required to assign ''F: GeoLink Geo-fence'' function in the ''General/Channels'' to an available channel.</translate>
{{Info|[[File:Info.png|18px|]] <translate><!--T:33-->
Please make sure that Geo-fence Area was defined. Four points must be programmed. The Spirit Settings will display right order to program all points.</translate>}}
=== <translate><!--T:80-->
Modes</translate> ===
<translate><!--T:81-->
If Geo-fence is engaged by assigned GeoLink channel there is possibility to use tri-state switch also for programming of a new Geo-fence area.
<!--T:82-->
When '''On (1)''' is displayed it mean that at this point Geo-fence is engaged and flight area is restricted. The model will return upon exceeding the area to the center of the area. Then pilot have to touch the aileron or elevator stick in order to continue in flight.
<!--T:83-->
When '''On (2)''' is displayed the unit is in a programming mode which allow to overwrite current Geo-fence to the new with position at which the model currently is. Please note that it will not work if model is flying or if GNSS signal is very weak.</translate>
<translate>If you will set '''Return Altitude''' parameter to a non-zero value then model will automatically reach and maintain this altitude when the function is engaged.</translate>
=== <translate><!--T:84-->
New Geo-fence programming</translate> ===
<translate><!--T:85-->
<!--T:86-->
If assigned GeoLink channel is used you have to set '''On (2)''' function state and keep it on for at least 2 seconds. At this period Status LED of the Spirit unit will turn off and after 2 seconds new Geo-fence point is programmed.
Pilot has to define four points that will determine new area. To program all four points pilot have to engage the programming four times.
Only once all points are programmed the Status LED of the Spirit unit will turn On which will signalize success. New area is applied immediately.
</translate>
== <translate><!--T:34-->
Altitude Limit</translate> ==
<translate>Altitude Limit is aid feature that can automatilly perform Rescue of the model as soon as it will drop under a specified altitude. Or it can stop the model ascending when it reach specified maximum altitude.
Altitude for the Hard Deck is programmed in two ways described in the '''Modes''' section above.</translate>
<translate><!--T:35-->
=== <translate><!--T:36-->
<translate><!--T:37-->
The feature can be engaged at any given time by a switch of your radio. We recommend to use a normal two-state or three-state switch for this feature. But first it is important to decide in which way the feature will be engaged as there are two options:
<!--T:38-->
# To engage with Stabi function - in this case the feature is engaged when programmed Stabi function is engaged. This mean you do not need to assign any other switch than when used for e.g. Stabilisation mode. ''[LESS CHANNELS ARE USED]''
# To engage with assigned GeoLink channel - it is required to assign ''F: GeoLink Altitude Limit'' function in the ''General/Channels'' to an available channel. ''[EASIER TO SET UP]''</translate>
Whenever the Altitude Limit feature is engaged it will first perform Rescue to notify you it was really engaged. At the same time you can use Altitude Limit as ordinary Rescue mode in case you forgot to engage it prior an unexpected situation.
=== <translate>Modes</translate> ===
<translate>
If Altitude Limit is engaged by assigned GeoLink channel there is possibility to use two different modes for activation.
In the Channels window you will be able to see Function as '''On (1)''', '''Off''' and '''On (2)''' which is corresponding to 100%, 0% and special case -1% to -100% channel value.
*When '''On (1)''' is displayed it mean that Hard Deck altitude is programmed from the altitude in which the model presently is. In other words, if you engage the Altitude Limit when flying in 5 meters, the models will be automatically recovered whenever it will drop under 5 meters. This mode is very easy to set, because you do not have to set basically anything. And additionally you can program Hard Deck to any altitude at any moment even without landing.
*When '''On (2)''' is displayed it mean that Hard Deck altitude is programmed from the channel value itself. It is calculated based on the range -1% to -100% where -1% is used for the lowest altitude and -100% for the highest altitude that is nearly equal to altitude specified for Maximum parameter.
As soon as you will enable mode On (2) you will also see exact hard deck altitude in the Aid Tab from GeoLink window. This will tell you in which altitude rescue will be performed.
</translate>
==== <translate><!--T:78-->
Triggering Acceleration</translate> ====
<translate><!--T:79-->
This parameter is key for engaging the Rescue mode fast enough if your model is approaching towards the ground.
The faster is descending velocity, the faster the Rescue is engaged. This mean that the Rescue can be engaged above configured Minimum limit to save the model safely. If model is approaching the Minimum limit slowly then the rescue is engaged at configured level.
Low Triggering Acceleration value is causing only minor difference.</translate>
== <translate><!--T:39-->
Return to Home</translate> ==
<translate><!--T:40-->
=== <translate><!--T:41-->
<translate><!--T:42-->
<!--T:43-->
# To engage with assigned GeoLink channel - it is required to assign ''F: GeoLink Return to Home'' function in the ''General/Channels'' to an available channel.</translate>
{{Info|[[File:Info.png|18px|]] <translate><!--T:44-->
Please make sure that Home spot was defined in the Map tab.</translate>}}
=== <translate><!--T:45-->
<translate><!--T:46-->
If Return to Home is engaged by assigned GeoLink channel there is possibility to use tri-state switch also for programming of a new Home spot.
In the Channels window you will be able to see Function as '''On''' and '''Off''' states.
When '''Off''' is visible the feature is not used in any sense. When '''On''' is visible you can enter several modes of the feature.</translate>
==== <translate><!--T:92-->
On (1)</translate> ====
<translate><!--T:47-->
'''Channel value 57% - 100%''' : When '''On (1)''' is displayed it mean that at this point Return to Home is engaged and model will move to the Home spot. This is what you might want to engage during flight.</translate>
==== <translate><!--T:93-->
On (2)</translate> ====
<translate><!--T:48-->
'''Channel value -100% - -62%''' : When '''On (2)''' is displayed the unit is in a programming mode which allow to overwrite current Home spot to the new with position at which the model currently is. Change will affect all Banks - if used. Please note that it will not work if model is flying or if GNSS signal is very weak.</translate>
==== <translate><!--T:94-->
On (3)</translate> ====
<translate><!--T:95-->
'''Channel value -61% - -38%''' : When '''On (3)''' is displayed the unit is in a programming mode which allow to overwrite current Home spot to the new with position at which the model currently is. Change will affect only active Bank - if Bank Switching is used. Please note that it will not work if model is flying or if GNSS signal is very weak.</translate>
==== <translate><!--T:96-->
On (4)</translate> ====
<translate><!--T:97-->
'''Channel value 27% - 56%''' : When '''On (4)''' is displayed it mean that at this point Return to Home is engaged and model will move to the Take-Off position. Take-Off position is programmed automatically during each Take-Off. This mode can be used stright with no Home position programming.</translate>
=== <translate><!--T:49-->
New Home position</translate> ===
<translate><!--T:50-->
<!--T:51-->
If assigned GeoLink channel is used you have to set '''On (2)''' function state and keep it on for at least 2 seconds. At this period Status LED of the Spirit unit will turn off and after 2 seconds new Home position is programmed. Once finished the LED must turn On again.</translate>
== <translate><!--T:87-->
Auto Landing</translate> ==
<translate><!--T:88-->
<translate><!--T:98-->
In order to make the landing as safe as possible set the Landing Speed value. We recommend to start with a low values and increase it to a speed that is suitable for the model. With too high value the landing might be too hard. Default value of 25̤̤% should work well for the most models.</translate>
=== <translate><!--T:89-->
<translate>
<!--T:90-->
<!--T:91-->
# To engage with assigned GeoLink channel - it is required to assign ''F: GeoLink Auto Landing'' function in the ''General/Channels'' to an available channel.</translate>
=== <translate><!--T:28-->
Geo-fence</translate> ===
== <translate><!--T:52-->
<translate><!--T:101-->
Position Hold</translate> ==
This feature allows to restrict flying area so that when flying over the model will return. Pilot can set a virtual fence in which the model is allowed to fly.</translate>
<translate><!--T:53-->
=== <translate><!--T:34-->
Altitude Limit</translate> ===
=== <translate><!--T:54-->
<translate><!--T:102-->
If you are worried you will forget to engage the Rescue mode in time, this feature is what you are looking for.</translate>
<translate><!--T:55-->
<!--T:56-->
=== <translate><!--T:39-->
Return to Home</translate> ===
# To engage with assigned GeoLink channel - it is required to assign ''F: GeoLink Position Hold'' function in the ''General/Channels'' to an available channel.</translate>
<translate><!--T:103-->
== <translate><!--T:57-->
<!--T:104-->
Altitude Hold</translate> ==
Visit [[GeoLink_Return_to_Home|Return to Home page]] to see all details about the function.</translate>
<translate><!--T:58-->
=== <translate><!--T:105-->
Auto Landing</translate> ===
<translate><!--T:106-->
Whenever you want to land with the model you can use this feature to do so automatically.</translate>
=== <translate><!--T:59-->
<translate><!--T:60-->
=== <translate><!--T:52-->
Position Hold</translate> ===
<!--T:61-->
<translate><!--T:107-->
If you are learning the basics this feature can help you significantly in maintaining required spot. If you are not strong in hovering the feature will do the job for you.</translate>
# To engage with assigned GeoLink channel - it is required to assign ''F: GeoLink Altitude Hold'' function in the ''General/Channels'' to an available channel.</translate>
=== <translate><!--T:62-->
<translate><!--T:63-->
=== <translate><!--T:57-->
If Altitude Hold is engaged by assigned GeoLink channel there is possibility to use tri-state switch also for disabling Collective Pitch input.
Altitude Hold</translate> ===
<!--T:64-->
<translate><!--T:108-->
If pilot is unable to maintain altitude the feature can control collective pitch automatically for him.</translate>
<!--T:65-->
When '''On (2)''' is displayed it mean that altitude in which the feature was engaged will be held. Pilot is unable to change Collective Pitch by pitch stick. So that Collective Pitch steering is fixed and is changed only by GeoLink in order to hold right altitude.</translate>
== <translate><!--T:66-->
Line 362: Line 200:
| style="width: 33%;text-align:center;"| [[#up|&uarr;<translate><!--T:74-->
Up</translate>&uarr;]]
| style="text-align:right;" | [[<translate><!--T:75-->
| style="text-align:right;" | [[<translate><!--T:109-->
GeoLink_Troubleshooting</translate>|<translate><!--T:76-->
GeoLink_Logging</translate>|<translate><!--T:110-->
Troubleshooting</translate> &rarr;]]
Logging</translate> &rarr;]]
Latest revision as of 13:38, 15 September 2022
1 GeoLink Support
2 Compass Calibration
All GeoLink modules were fully tested and calibrated. The only thing pilot might need is to re-calibrate Compass. Compass is crucial for determining heading of the model for a proper navigation through space. Compass is sensing Earth's magnetic field (Geomagnetic field) and in this way it can determine heading at any time. Unfortunately Geomagnetic field is different everywhere. Thus if model will be operated outside the Czech Republic it is highly recommended to perform New Calibration. GeoLink modules are factory calibrated for the Czech Republic.
2.1 How to check
Info.png We recommend to not use a smart devices for compass heading comparison. These are usually not calibrated at all nor allow the calibration. An analogue compass is the best for comparison.
2.2 Odd behavior
2.3 Calibration process
Info.png For 600+ class helicopters we recommend to perform calibration while GeoLink is not mounted. In that way it can be more comfortable and easier.
Info.png Calibration should be done ideally at the flying field but can be performed usually indoor as well.
Warning.png Spirit Setings will not see GeoLink during Calibration mode. Calibration will not finish until it is fully done. If power is turned off while calibration is not finished, the calibration process will start from the beginning after next power up.
2.4 Calibration Video
3 How to configure
3.1 Triggering
3.1.1 Stabi function
By default all GeoLink features are engaged as soon as a Stabi function is active. For example if Coaxial or Rescue mode is engaged the GeoLink feature is engaged as well and complement operation of a Stabi function by acting simultaneously. We recommend to set Stabi/Function to Coaxial mode for Geo-fence, Return to Home and Position Hold features. We recommend to use this way only when you are out of a free channels.
4 GeoLink functions
4.1 Geo-fence
4.2 Altitude Limit
4.3 Return to Home
4.4 Auto Landing
4.5 Position Hold
4.6 Altitude Hold
5 Correction Gains
5.1 Horiontal Gain
5.2 Vertical Gain