Difference between revisions of "Governor"
Line 68: Line 68:
* [[<translate><!--T:15-->
Spartan SRC-RPM RPM Sensor</translate>]]
== <translate>Setup</translate> ==
=== <translate>Electric</translate> ===
<translate>#Set throttle range in your transmitter so that 0% and 100% throttle position matches with value of the Throttle bar in the Diagnostics tab. This can be done by Subtrim function in your transmitter and/or Travel Adjustment function.
#Re-calibrate throttle range according the instructions of your ESC. In the most cases it can be configured by powering the model with throttle stick with 100% throttle and then by moving the stick down to 0%. This can be done only when Spirit Governor is disabled.
#If possible, configure fast spoolup mode in the ESC so the governor spoolup procedure will not interfere with ESC.</translate>
=== <translate>Nitro / Gasser</translate> ===
: <translate>Set the throttle range in your transmitter so that 0% and 100% throttle position matches with value of the Throttle bar in the Diagnostic tab. This can be done by Subtrim function in your transmitter and/or Travel Adjust function.</translate>
== <translate>Activation</translate> ==
<translate>To activate Governor feature in the unit, you will need to assign Throttle function in the General tab/Channels. Then you will be able to enter Governor Settings in the General tab.</translate>
<translate>To activate Governor feature in the Spirit unit, you will need to assign Throttle function in the '''General tab/Channels'''. Then you will be able to enter Governor Settings in the General tab.</translate>
== Spirit Settings ==
<translate>First from all basic settings are necessary so the governor can control the head speed correctly.</translate>
<translate>First from all basic settings are necessary so the governor can control the head speed correctly. Please review all the parameters prior any configuration.</translate>
[[File:<translate>Goven.png</translate>|center|500px]]
Line 147: Line 136:
<translate>Prevents from prolonged overspeeding after demanding maneuvers. If head speed is higher than requested after demanding maneuver then by decreasing percentage value it is possible to shorten or eliminate this odd behavior. If Limit value is too low then Holding Performance will not affect Governor performance. It is recommended to use 80% for the most helicopters. Usually combustion helicopters might need to decrease the Limit. Changing the Limit as the last parameter of the Governor is recommended - once a proper Governor Response and Holding Performance values are configured.</translate>
== <translate>Transmitter</translate> ==
== <translate>Throttle Channel verification</translate> ==
<translate>Set the Throttle Range in your transmitter so that 0% and 100% throttle position matches with value of the Throttle bar in the Diagnostic tab. This can be done by Subtrim function in your transmitter and/or Travel Adjust function.
When 0% or 100% throttle curve value in your radio is configured and Diagnostic tab in the Spirit Settings will show the same, then Throttle channel in your radio is configured well.
</translate>
== <translate>Electric motors - ESC Setup</translate> ==
=== <translate>ESC Throttle Calibration</translate> ===
<translate>Before you can use Spirit Governor, Throttle Range in the Spirit and ESC must match with each other. For this purpose Throttle Calibration is performed.
For the most ESCs you can find out what factory Throttle signal range is. If you know these two values (usually near 1100 - 1900) you do not have to perform Throttle Calibration.
Each ESC manufacturer can have a slightly different values. If you will set these values in the Spirit unit, then the throttle range should match perfectly.
If you performed Throttle Calibration in the past then the following procedure is necessary.
#Turn off Spirit Governor in order to perform Throttle Calibration.
#Set linear Throttle curve in your radio transmitter so that 0% and 100% throttle position matches with value of the Throttle bar in the Diagnostics tab. If it is not matching, use Subtrim function in your transmitter and/or Travel Adjustment function.
#Re-calibrate Throttle Range according the instructions of your ESC. In the most cases it can be configured by powering the model with throttle stick with 100% throttle and then by moving the stick down to 0%.
#Now you can enable Spirit Governor again.
</translate>
=== <translate>ESC setup</translate> ===
<translate>To obtain good performance, configure fast spoolup mode in the ESC so the governor spoolup procedure will not interfere with ESC.
Some ESC offer specific settings for External Governor. Please set mode recommended by ESC manufacturer.</translate>
== <translate>Combustion motors - Throttle Servo Setup</translate> ==
<translate>Please set Throttle Range and Throttle Reverse parameters in the Spirit Settings software to match carburator range precisely.</translate>
== Radio Setup - Throttle Curve ==
<translate>Flat Throttle Curve above 50% is necessary in order to use Governor feature. Under 50% Governor is immediately disarmed and instead motor will be driven directly by throttle curve. As soon as it will exceed 50% spoolup procedure is engaged until Requested RPM is reached.
Revision as of 17:21, 11 September 2020
The governor from the Spirit unit (so called External governor) can be used with all single line digital receiver connections.
This mean that for PWM and PPM it cannot be used. To make it work, you will need to get a RPM Sensor which can supply the unit with current RPM data.
1 Wiring
1.1 Throttle
For usage of the Spirit Governor it is necessary to connect the Throttle (ESC or the Throttle servo) to the following port:
  • Spirit and μSpirit - AUX port
  • Spirit Pro and Spirit 2 - AUX1 port
  • Spirit RS - THR port
1.2 RPM signal
To make the governor work well it is very important to choose an appropriate RPM sensor. RPM sensor can be external or built-in in the ESC.
Cable that carry RPM signal must be always connected when Governor is used.
Connect RPM signal cable to the pin of the unit:
  • μSpirit - P pin - pin in the middle of P/E/A port
  • Spirit - PIT pin - pin in the middle of ELE/PIT/AIL port
  • Spirit Pro and Spirit 2 - PIT pin - pin in the middle of ELE/PIT/AIL port
  • Spirit RS - RPM pin - pin in the middle of EXT/RPM/E2 port
Sensor can be powered from any available Satellite port (SAT) or directly from a BEC. Satellite port is giving 3.3V, while BEC is operating usually at 5 - 8V.
1.3 Wiring example
2 List of tested sensors
The following are known to work well.
Electric Motors
Nitro and Gasser Motors
3 Activation
Fine-Tuning - Holding Limit
5 Throttle Channel verification
6 Electric motors - ESC Setup
6.1 ESC Throttle Calibration
  1. Turn off Spirit Governor in order to perform Throttle Calibration.
  2. Set linear Throttle curve in your radio transmitter so that 0% and 100% throttle position matches with value of the Throttle bar in the Diagnostics tab. If it is not matching, use Subtrim function in your transmitter and/or Travel Adjustment function.
  3. Re-calibrate Throttle Range according the instructions of your ESC. In the most cases it can be configured by powering the model with throttle stick with 100% throttle and then by moving the stick down to 0%.
  4. Now you can enable Spirit Governor again.
6.2 ESC setup
7 Combustion motors - Throttle Servo Setup
For a Combustion motors we recommend to go from Idle RPM (Throttle Curve around 10%) directly to 50% flat curve and above. This will trigger smooth spoolup.
9 Fine-Tuning Procedure
10 Autorotation Bailout
  • When doing autorotation do not engage the Throttle Hold.
  • Use an assigned switch instead, that will set the Throttle Curve to somewhere between 12 - 50%.
Info.png If Throttle Curve will drop under 12% the spoolup will be normal.
11 Throttle Hold for Autorotation (optional)
  1. Set the Throttle Curve for Hold to 12%. (This will spin-up the motor)
  2. Decrease General/Governor/Throttle Range - Min. until the motor will stop completely.
  3. Increase the Spoolup Rampup until you will get immediate spoolup when Hold is disarmed.
12 Troubleshooting
  • A delay between disarming Throttle Hold and motor rotation - motor will start to spin after a short time.
Make sure that your Throttle Range was configured correctly. Did you calibrated the throttle range with the Spirit connected?
We recommend to put the ESC into the Factory settings. In the most cases the default range is matching with preconfigured range in the unit (1100μs - 1900μs).
In case that the range is configured correctly, but there is still a noticeable delay, please increase the Spoolup Rampup parameter until the motor will start to spin instantly after disarming the Hold switch.
  • Motor will kick after disarming the Hold switch causing unwanted rotation of the model.
Decrease the Spoolup Rampup parameter until the kick will disappear. If you will notice a delay before spooling, the value is too low now and other solution must be used. In this case the problem cannot be solved by any settings of the Spirit unit.
Check if the ESC supports a Spoolup Power parameter. If it is supported, then try to decrease the power and observe if it will help you. In some cases a different Timing or PWM frequency can help, but always make sure that the settings are valid for your motor.
  • After demanding maneuvers the head speed is maintained at higher RPM for prolonged period.
Verify that the Throttle Range of your ESC or Throttle servo is configured properly. Usually the problem is caused by exceeded limit for the full throttle defined by Throttle Range - Max. value. For example, if the top limit in the ESC is programmed to 1800μs but the unit has configured 1900μs, then the unit will be 100μs over the real limit. Thus during a high load it could take a few seconds until the value will drop under 1800μs in this case.
Correct solution is to reconfigure the Throttle Range either in the ESC or in the unit.
  • There is often "RPM Sensor data are too noisy" event in the flight log.
Make sure that the connection of the RPM Sensor output is good. If the RPM Sensor is separated from the ESC, please connect its power supply (especially the grounding wire) as close as possible to the RPM signal wire in the unit. Usage of a ferrite rings for the power supply could reduce a noise as well. Verify operating voltage requirements for the sensor. Some sensors require 3.5V or more so they can't be powered from the Spektrum port of the unit. In some cases it is caused by too high Governor Response value, because motor will start to jitter.
  • Governor is not switching between different throttle curves.
Your Throttle Range in the ESC is calibrated incorrectly - range that unit is programmed for is not matching range of the ESC. Correct calibration of the range will solve the problem.
  • RPM signal was lost.
If Governor will loose the signal, it will detect the event within 2 seconds. Governor will still work, but with worsened performance - similarly as with a V-curve. This event can happen, if the signal cable connection will fail. For this reason we highly recommend to use a hot glue or other way for securing the connections.